Each switchboard used asservice equipmentmust be provided with amain bonding jumper.

Suggested Answer: A Vote an answer

A main bonding jumper is required to connect the grounded conductor (neutral) to the equipment grounding conductor at the service disconnect. This establishes a low-impedance fault return path necessary for overcurrent devices to operate promptly. NETA Level 2 technicians must verify proper bonding during acceptance and maintenance inspections because improper bonding can lead to elevated touch potentials and ineffective fault clearing.